3/15/2012 6:03 PM
I've been dealing with a very frustrating electrical issue for the past 4 days. One of the 120v lines that powers 10 of my clocks (Rainbird Par+) keeps tripping the breaker (20a). It can take anywhere from 2-10 hours for this to happen after re-energizing the circuit breaker. I've checked every splice/junction on the run and for voltage get 115-118v on the hot, 0-0.1 on the ground and at the closest clock from the circuit breaker get 1-1.5v on the neutral with the voltage increasing on the neutral the farther I get from the circuit breaker(2nd clock 2v, 3rd clock 2.8v, 3rd, 4th, 5th clocks(on lateral lines from main power) reading 3.2-3.5, 6th clock 6v, 7th & 8th clocks 7.1v, 9th clock 8.5 and the 10th clock reading at 10v. Obviously if it was a dead fault then it would be easy to find, but I'm thinking I dealing with a possible fault to earth ground....maybe a small nick in the hot wire wire...I don't know.
We thought that we might have a transformer(s) going bad in a clock so I installed 1a circuit breakers in all the clocks and none of those have tripped. We tested the amp load at the power source and the line was only drawing 2.2a under no load. Almost every time the breaker has tripped it has not been under load. I installed a new 20a breaker. Running out of ideas.
I've had one of my members who, is a electrician, look at it and he is baffled also. He is going to try and get a hold of the megometer his company has and see if this can help find the problem.
Any ideas or suggestions are welcome......I'm begging you!! LOL.